No Control Builder target in Configuration Studio


#1

The installation was done as a SCADA install, rather than a Process install. When choosing the node type, the C200/300, ACE, SIM check box was unchecked.

The installation type can be confirmed via the 2 following registry entries.
SCADA installation, Flex.
[HKEY_LOCAL_MACHINE\SOFTWARE\Honeywell\TPS50\InstallInfo"InstallProductKey"=“SCADA Client”
[HKEY_LOCAL_MACHINE\SOFTWARE\Honeywell\TPS50\InstallInfo\Engineering Tools\ “IsCDA”=“No”

Process installation, Flex.
[HKEY_LOCAL_MACHINE\SOFTWARE\Honeywell\TPS50\InstallInfo"InstallProductKey"=“Process Client”
[HKEY_LOCAL_MACHINE\SOFTWARE\Honeywell\TPS50\InstallInfo\Engineering Tools\ “IsCDA”="Yes”

SCADA installation, Server.
[HKEY_LOCAL_MACHINE\SOFTWARE\Honeywell\TPS50\InstallInfo"InstallProductKey"=“SCADA Server”
[HKEY_LOCAL_MACHINE\SOFTWARE\Honeywell\TPS50\InstallInfo\Engineering Tools\ “IsCDA”=“No”

Process installation, Server.
[HKEY_LOCAL_MACHINE\SOFTWARE\Honeywell\TPS50\InstallInfo"InstallProductKey"=“Process Server”
[HKEY_LOCAL_MACHINE\SOFTWARE\Honeywell\TPS50\InstallInfo\Engineering Tools\ “IsCDA”="Yes”

SCADA installation, Console Station.
[HKEY_LOCAL_MACHINE\SOFTWARE\Honeywell\TPS50\InstallInfo"InstallProductKey"=“SCADA Station”
[HKEY_LOCAL_MACHINE\SOFTWARE\Honeywell\TPS50\InstallInfo\Engineering Tools\ “IsCDA”=“No”

Process installation, Console Station.
[HKEY_LOCAL_MACHINE\SOFTWARE\Honeywell\TPS50\InstallInfo"InstallProductKey"=“Process Station”
[HKEY_LOCAL_MACHINE\SOFTWARE\Honeywell\TPS50\InstallInfo\Engineering Tools\ “IsCDA”="Yes”

Note: The “[HKEY_LOCAL_MACHINE\SOFTWARE\Honeywell\TPS50\InstallInfo"InstallProductKey” may vary between releases.