Fire resistance tests


#1

The classification of fire resistance of materials and structural assemblies is generally determined by tests. Standardized fire resistance tests have traditionally been used for structural assemblies and structural components. These tests, which include furnace exposure tests and direct fire / burner exposure tests, are described here:

Furnace exposure test:

Furnace exposure test is entailed to subject the structural assembly of the equipment with Temperature-time graph. The cause in equipment or components is verified by changing the temperature by regulating the furnace fuel and air flow rates.

The temperature-time curves adopted by the International Standards Organizations (ISO 834, 1975), the American Society for Testing and Materials (ASTM E-119, 1983), and the British Standards Institution (BS 476-1972).

Two important complications inherent in the use of standard temperature-time exposures are:

  • differences between the anticipated enclosure fire temperature development and the furnace
    temperature-time curve
  • furnace heat fluxes on the test assembly depend on other factors besides furnace gas temperature.

The successful fire resistance is based on either excessive heat transmission or structural failure. Excessive heat transmission is measured in terms of the temperature of the unexposed side of the assembly. The structural failure is measured by the specified maximum acceptable temperature.

Empirical correlation

The following correlations are intended to provide estimates of the expected fire resistance measured in furnace exposure tests with different types of exposed structures. A more complete set of correlations and standard calculation methods for fire barrier assemblies made of either structural steel, various forms of concrete, masonry, or timber and wood, has been compiled by ASCE and
SFPE (1995).

Steel columns – Unprotected steel columns have been found to have furnace endurance times
proportional to (W/D)n, where W is column weight per unit length (Ms/L), D is the heated perimeter of a column section, and n is an exponent equal to 0.7 for W/D < 10 lb/ft-in, and to 0.8 for W/D > 10 lb/ft-in.

Steel beams – The fire resistance of steel beams has been found to vary with the parameter.

h(W/D + 0.6)

where h is the thickness of a particular spray-applied insulation (in), W is the weight of the beam per lineal foot (lb/ft), and D is the exposed perimeter of the beam cross-section (in).

Concrete slabs – The fire endurance of concrete walls and floor slabs depends upon the wall/slab thickness, type of aggregate, steel reinforcing properties, the applied load, and the type of restraints. Fleischmann (1995) has reviewed the analytical and empirical methods for evaluating these effects.

Wood structures – The fire resistance of an exposed wood structure is limited by the rate of wood charring since the char has essentially no load-bearing capacity. According to White (1995), charring occurs when the heated wood temperature reaches about 290 ◦C (554 ◦F), and there is a steep temperature gradient in the uncharred wood. Therefore, most of the uncharred wood remains cool enough to retain its original strength.

High-intensity fire resistance test:

ASTM P-191 (1986) describes a high-intensity fire test for structures (columns, beams, and walls) exposed to hydrocarbon liquid pool fires. A total heat flux of 173 ± 8 kW/m2 (15.2 ± 0.7 Btu/sec-ft2) must be reached in five minutes and maintained for the duration of the test. This heat flux is supposed to be generated with a gas temperature of 927 to 1260 ◦C (1700 to 2300 ◦F) and a gas velocity of 10 m/s (33 ft/s).