How to connect 4 wire RTD to PLC?


#1

How we can connect 4 wire RTD to PLC cards?


#2

Two Options are there to connect 4 wire RTD to PLC.

First option is to use RTD-mA converter.

RTD-mA converter (Transmitter) is usually a better option that wiring RTD directly to the PLC card.

There are advantage of using this method.

1.Reduce the cost by not using a different type of PLC input card.
2.Some PLC card do not allow individual calibration of RTD channels.

2nd method of connecting 4 wire RTD to PLC input.

It is possible to connect a 4 wire RTD to a 3 wire input by just not connecting the sense wire. You can also connect to 2 wire input by not connecting either sense wires.